View Full Version : Timeoverdue alarm
Is there anyway I can disable this? My top up keeps not running as the Timeoverdue water 1 is ticked a lot of the time.
Auto top off is set to 2secs and a max on-time of 45 seconds
stevew@reefdreams
28-05-09, 21:44
Those are quite strange settings you have, the setting for auto top off is the time after the sensor first triggers before the sensor is deemed to be active, 2 secs is quite short and the ripples from topping off could easily trigger this. I would suggest setting this to at least 10 secs as does it really matter if the water level is low for 10 seconds?
The max on time is again quite short at 45 secs, is your pump capable of topping up in 45 seconds?
I would extend the max on time setting before disabling the setting all together as you really don't want a flood.
If you do want to disable it completely then set it to all zeros.
Steve
thanks I will try these new settings out.
I cannot work out what purpose the function actually serves!